Hi everybody.
I have Ecotec Bioline 20 and it already works normal at 8 years. I clean ash from all system aprox. 1 time in every month and system works very well
But this winter start problems.
Right now comes every day 1-2 times "Hot Stock Pipe Error". I don't know what to do.
In Estonia we don't have anymore Ecotec dealer eather.
EcoTec Bioline 20 problem ?
-
- Pannrumsfanatiker!!!!
- Inlägg: 5015
- Blev medlem: sön 22 jan, 2012 11:20
- Ort: Kungsbacka
Re: EcoTec Bioline 20 problem ?
Never heard about that alarm before. Maybe it´s like "back heat".
Do you have to reset the termal contact pos. 18 at page 4 in the manual? http://www.wv.fi/folder/Bioline_20manual713.pdf
Check if the gate wings are worn.
Check also if the short pipe between the input feeder pipe and the air distribution box is clogged.
You can see this pipe on the first picture at page 4.
Clean the pipe with a wire. You have to dismount the fan to do this.
Do you have to reset the termal contact pos. 18 at page 4 in the manual? http://www.wv.fi/folder/Bioline_20manual713.pdf
Check if the gate wings are worn.
Check also if the short pipe between the input feeder pipe and the air distribution box is clogged.
You can see this pipe on the first picture at page 4.
Clean the pipe with a wire. You have to dismount the fan to do this.
Optiburn -22, Värmebaronen Combimax 2000 UB -94, Ulma doserskruv, ack Thermia SA500B, Thermomatic CBJ, 3 ton bulkförråd
Värmer 240m²(2pl) + 90 m² källare
Värmer 240m²(2pl) + 90 m² källare
Re: EcoTec Bioline 20 problem ?
When you allready have the fan away, take a toothbrush and clean the wings of the fan.
Stenhus från -58, Thermia Biomatic -03, Ecotec Bioline 20 -05, Thermomatic EC Home, EVR-C. Egensotare.